Im currently designing a network, where i would have like to put 3 off 740kW motors with VSD's. This would have been kinder to the network upon start up, but also provide a 'barrier' to stop these motors contributing to any fault which occurs on the network.
However, due to factors outwith my control, we cannot have VSD's on the network, but the fault levels seen on the MCC busbars go up to a level just over the designed fault rating of the installed busbars (using ETAP computer model, busbars rated for 100kA 1 sec).
Do softstarts give the same protection?
When the bypass contactor is in operation there is short-circuit current contribution from the connected motor to the input side.
But newer types of softstart do not utilise a conventional mechanical bypass contactor. Some use solid state/electronic means to fulfill the bypass duty.
The Allen Bradley SMC-Flex has the 'integral' bypass, but via solid state/electronic means.
Has anyone ever encountered this type of problem before?
Simon
However, due to factors outwith my control, we cannot have VSD's on the network, but the fault levels seen on the MCC busbars go up to a level just over the designed fault rating of the installed busbars (using ETAP computer model, busbars rated for 100kA 1 sec).
Do softstarts give the same protection?
When the bypass contactor is in operation there is short-circuit current contribution from the connected motor to the input side.
But newer types of softstart do not utilise a conventional mechanical bypass contactor. Some use solid state/electronic means to fulfill the bypass duty.
The Allen Bradley SMC-Flex has the 'integral' bypass, but via solid state/electronic means.
Has anyone ever encountered this type of problem before?
Simon