I have a question regarding the soil resistivity measurement. Soil resistivity for the ground grid system of high voltage (HV) substations is measured as per IEEE-81. How about transmission lines, is it required that the soil resistivity be measured at the base of each tower of high voltage transmission line? Thanks.
 
Replies continue below

Recommended for you

I do not believe it is required. When calculating step and touch potential formulas at the substation, sometimes a split factor estimation is used for 4 wire distribution lines or transmission lines with OPGW's, which is where pole grounding resistance would come into play. But these are just conservative estimations mostly. I usually just look at what is the type of soil along the terrain that produces the worst resistivity values and just use the value for that from a table. If someone is looking for a more accurate idea of how the current splits for certain faults, the proper way to quantify it would be to actually measure it using clamp on CT's.
 
If you are designing the transmission line, it would be helpful to measure soil resistivity at a few points along the line route. The readings would be used to design structure grounding to meet the requirements for lightning protection. You don't need a measurement at each pole, but enough to get a good average along the line.

As 9wearSuave said, if you are designing the substation grounding, what is needed is structure ground resistance to determine fault current return splits.
 