Does anyone know where to find a design manual for calculating the sectional modulus for a soldier pile wall with a raker for a 14 foot high wall, soldiers at 7 feet on centre, raker about 2 feet from the top with a 50 psf surcharge?
 
Replies continue below

Recommended for you

Try the Caltrans Shoring and Trenching Manual. Note, though, that shoring movement checks aren't performed, but you should perform one anyway.


If you want you can place a waler between piles and a raker every 14 feet with a roll chock. This will help excavation activity (more space for excavator).

Are you adjacent to an existing building? Prefer tiebacks over rakers in this situation.
 
VictorAK,

The raker acts as a strut (assuming that you've sized it correctly for the required loads). It's a straightforward problem for a nongravity wall. See FHWA guidance for determining braced wall earth pressures and anchor/strut loads here:


Most use software to perform the wall analysis.

Jeff
 