Solenoid Valves

Status
Not open for further replies.

g1a1

Mechanical
Nov 21, 2001
29
Looking for a 3-way, S/S, Normally Closed, 12vdc-low power Pneumatic Solenoid Valves for -40F service. One at a Cv=0.7 min and the other at a Cv=3.00 min. It must exhaust a 2" and 8" (respectively) ball valve equipped with a actuator(port=0.7Cv and 3.00Cv) in 2.0 sec or less. I have tried some off-the-shelf solenoids rated to -40F, but closing times at -40F were too slow. Ambient speeds were OK. I have surfed the web and have made numerous contacts, but have not had any success. I would appreciate any assistance.
Thanks
 
Replies continue below

Recommended for you

G1a1
I'm working for years now with Pneumatic valves as Turbine control valves and Stop valves. We got closing time of 1/3sec for 12 - 20" stop valve and 0.7 to 1.2 sec for control valve.
For ON/OFF valve I use the solenoid to operate 1/2" pneumatic pilot valve in combination with quick exsaust valves to get the high speed emergency close.
For analog valves I use volume boosters (one for each side of the actuator) it is very expensive (more then 1,000$ for the two boosters, 3/4" pipe diameter) but it gives the results and it cheaper then Hydraulick system.
If you need vendor list, please write and I will collect it.
Cheer up
ilan
 
Thanks ilan. I think the quick exhaust may solve my problem.
 