tunemeister
Electrical
- May 6, 2004
- 2
We have a (installed 35 years ago) 13.8 kV 25 MVA generator (peaker) resistively grounded through a grounding transformer and resistor with a voltage relay to detect ground faults down to 5% of the generator winding which is typical of utility grid connected generator units. The generator feeds a 13.8 kV breaker and then only a generator stepup transformer (GSU) to 120 kV. Unfortunately, we intalled a standard distribution substation transformer with the delta connection on the 120 kV and a wye connection on the 13.8 kV and have solidly grounded the 13.8 kV (the standard practice for 13.2 kV distribution substation transformer installations). Typically, GSU transformers are delta on the low side to keep the generator ungrounded and wye on the high side to act a ground source into the bulk power system with grounding connected as needed. A high end generator ground fault current contribution from our system is calculated to be 7700 amps and should be cleared with a relay and breaker time of 7 cycles. What kind of damage can be expected for a ground fault in the high end of the generator with this fault amperage and clearing time.
I am trying to present a case to unground the 13.8 kV transformer neutral and install ground fault relaying on the transformer side of the generator breaker to se ground faults when the breaker is open. If this (or some other fault) will do significant damage to the generator to require more extensive repairs (steel core damage requiring core rebuilding or more expensive rewinding) then the changing of the transformer neutral connection is warranted.
I am trying to present a case to unground the 13.8 kV transformer neutral and install ground fault relaying on the transformer side of the generator breaker to se ground faults when the breaker is open. If this (or some other fault) will do significant damage to the generator to require more extensive repairs (steel core damage requiring core rebuilding or more expensive rewinding) then the changing of the transformer neutral connection is warranted.