Hi,
We have a 230V motor space heater power cable and a shielded thermistor cable to enter into motor terminal box in one cable entry.

Please provide your thoughts and recommendations. Thanks
 
Replies continue below

Recommended for you

Dear Mr. Histor (Electrical)(OP)15 Jan 23 12:20
"....We have a 230V motor space heater power cable and a shielded thermistor cable to enter into motor terminal box in one cable entry...."
I am of the opinion:
(a) it is fine, if the shielded thermistor cable is rate for >230V say 400V.
(b) otherwise, they shall be in separate metallic or PVC conduits.
(c) A single metallic duct with metallic partition separating the two circuits are also acceptable.
Che Kuan Yau (Singapore)
 
Histor: Please check with your corporate specifications AND with your local authority having jurisdiction (national electric code). You might find that you require spatial distance and/or physical barriers separating "data" level signals (< 25 V) from low voltage (25 - 480 V) and both of those from higher voltage levels. You may also find that there is a requirement to separate "power" cables from "instrument" cables, regardless of voltage level.