ScottyUK
Electrical
- May 21, 2003
- 12,915
Could someone give me a quick sanity check?
One of our switchboards has a fairly complex old-school summation CT scheme feeding metering, and I need to remove a couple of circuits from the scheme. The scheme uses a number of summation CTs, each with multiple 5A primaries and a single 5A secondary. Several of these summation CT secondaries drive a further summation CT which then feeds into an energy meter.
We all know that a short-circuit is always applied to an unused CT secondary winding to prevent damage to the CT and avoid hazardous voltages being developed. In the case of this summation CT I will have an unused primary winding. I think we should leave it open, because shorting it will effectively turn it into an additional secondary winding and reduce the available ampere-turns available to drive current in the proper secondary winding, which will cause the meter to under-record the energy usage. The counter opinion expressed is that the spare primary should be shorted for safety like an unused CT secondary, but I think they are saying this because "you always short an unused CT winding" without considering that this is a primary winding and not a secondary.
Am I losing my marbles?
One of our switchboards has a fairly complex old-school summation CT scheme feeding metering, and I need to remove a couple of circuits from the scheme. The scheme uses a number of summation CTs, each with multiple 5A primaries and a single 5A secondary. Several of these summation CT secondaries drive a further summation CT which then feeds into an energy meter.
We all know that a short-circuit is always applied to an unused CT secondary winding to prevent damage to the CT and avoid hazardous voltages being developed. In the case of this summation CT I will have an unused primary winding. I think we should leave it open, because shorting it will effectively turn it into an additional secondary winding and reduce the available ampere-turns available to drive current in the proper secondary winding, which will cause the meter to under-record the energy usage. The counter opinion expressed is that the spare primary should be shorted for safety like an unused CT secondary, but I think they are saying this because "you always short an unused CT winding" without considering that this is a primary winding and not a secondary.
Am I losing my marbles?