I have two identical 4000hp Synchronous Motors operating reciprocating compressors. The ‘–ve’ terminal brushes on one machine tend to develop spark. The excitation control system (GE-Stat-x-ator) has almost the same volts/amps/pf for each machine, as the loading is identical. Need help to find root-cause for the carbon-brush spark?
 
Replies continue below

Recommended for you

First thoughts:
rough slip ring causes bouncing
not enough spring tension
brush face condition

Is it a condition that developed over time?

=====================================
Eng-tips forums: The best place on the web for engineering discussions.
 
No mechanical/maintenance type issues. New brushes/slip-rings/holders installed 3-4 weeks back. Enclosed & instrument air for cooling. Each time set of brushes on ‘-ve’ terminal develop spark.
 
A former employer used to have problems with some sliprings arcing. The sliprings were exposed to a somewhat corrosive atmosphere and had tiny little surface pitting. They started re-facing the sliprings with a different metal.

Another client had problems with only one brush of the two on one slipring arcing. The problem was that the installer had not installed a jumper to equally share the current between the two brush-holders.

Another problem surfaced when we found that an ambitious electrician had "re-sized some off the shelf brushes from generator exciter service to make them fit the synchronous motor application. After all, it was "all black carbon, right?" Wrong composition=arcing.