Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

Special confinement for columns in AS3600

Status
Not open for further replies.

asixth

Structural
Feb 27, 2008
1,333
0
0
GB
I don't like the all or nothing approach of the special confinement requirements in AS3600.

I agree with the no special requirements under fc=50MPa and a confinement of 0.1*fc above 0.75*phi*Nuo. But I think it should have an intermediate confinement requirement between these two values of 5MPa. Please see the attached diagram.
 
 http://files.engineering.com/getfile.aspx?folder=11a3ed8a-e6d3-415e-b432-d9f5901e03b6&file=Confinment_Diagram.pdf
Replies continue below

Recommended for you

Asixth,

You still need confinement in those areas based on the general confinement rules in clause 10.7.4 and table 10.7.4.3. It is just not based on a strength calculation as is required for the Special Confinement zones in Fig 10.7.3.1(A).
 
Status
Not open for further replies.
Back
Top