Steve-M
Mechanical
- Aug 11, 2016
- 4
thread378-416204
The poster for the original thread referenced above was trying to standardize the information contained in some internal company database for the various fittings used in their building. Part of the challenge was when to include pipe schedules as relevant information.
This post is a word of caution regarding pipe schedules. My Tioga Pipe chart lists (3) different columns of information under the same "schedule designation" heading. Anecdotally, I think these different schedule names came from the different industries that all used pipe. Depending on who you are talking to, you may hear any or all of the designations get used.
Many different pipe schedule designations can refer to the same wall thickness of pipe. But, this is not true for all designations in all sizes. For example, in Nominal Pipe Sizes (NPS) 8 and smaller, Sch.STD = Sch.40 = Sch.40S and Sch.XS = Sch.80 = Sch.80S. When you reach NPS 10, the rules change. The NPS 10 Sch.STD = Sch.40 = Sch.40S is still true. But, NPS 10 Sch.XS = Sch.80S = 0.500" wall thickness, which does not equal NPS 10 Sch.80 = 0.594" wall thickness.
It may not be necessary to provide a wall thickness along with the schedule designation on smaller pipe sizes. But, including it can save confusion (and huge headaches) when you get into larger sizes. As one poster said, (paraphrasing) "it is better to give someone more information", they can always disregard the extra details. But, when you don't give them enough, you are forcing them to guess/make up those details or contact you for the rest of the information they need. The latter is a waste of time. The other is dangerous.
Steve
Quote: "Sometimes, the biggest problems are caused by the smallest things. Pay Attention!" (Unknown)
The poster for the original thread referenced above was trying to standardize the information contained in some internal company database for the various fittings used in their building. Part of the challenge was when to include pipe schedules as relevant information.
This post is a word of caution regarding pipe schedules. My Tioga Pipe chart lists (3) different columns of information under the same "schedule designation" heading. Anecdotally, I think these different schedule names came from the different industries that all used pipe. Depending on who you are talking to, you may hear any or all of the designations get used.
Many different pipe schedule designations can refer to the same wall thickness of pipe. But, this is not true for all designations in all sizes. For example, in Nominal Pipe Sizes (NPS) 8 and smaller, Sch.STD = Sch.40 = Sch.40S and Sch.XS = Sch.80 = Sch.80S. When you reach NPS 10, the rules change. The NPS 10 Sch.STD = Sch.40 = Sch.40S is still true. But, NPS 10 Sch.XS = Sch.80S = 0.500" wall thickness, which does not equal NPS 10 Sch.80 = 0.594" wall thickness.
It may not be necessary to provide a wall thickness along with the schedule designation on smaller pipe sizes. But, including it can save confusion (and huge headaches) when you get into larger sizes. As one poster said, (paraphrasing) "it is better to give someone more information", they can always disregard the extra details. But, when you don't give them enough, you are forcing them to guess/make up those details or contact you for the rest of the information they need. The latter is a waste of time. The other is dangerous.
Steve
Quote: "Sometimes, the biggest problems are caused by the smallest things. Pay Attention!" (Unknown)