Thank you colleagues for your guidance.
It is a steel stair free standing for two landings. The owner does not want the stair attached on the 2nd and 3rd floors landings. In the architectural drawings the architect is proposing a 5" circular column, that based on the loads per step it will be enough as per the aisc manual.
I am treating it as single cantilivered steps. But my real question is: When the stair is in full use, that would be a full evacuation of the building, I am assuming one person per step, we are creating 28 small simultaneous moments that as Carlbauer in his post said we could consider 1KN per step. How will be the column designed?
Another consideration would be having people standing on just one side of the stair, creating a similar moment that would be aplied on the column at the steps intervals, forcing some sort of buckling stresses on the steel column.
Again, any ideas?