Hi everybody !

I have to design an aluminum mullion (rectangular tube) to span continuous between atleast 2 floors (4.2m span each atleast). The mullion has to be spliced at every floor level (point of support on to the floor). The splicing proposed, is to insert a sleeve inside the lower mullion and to bolt it. The upper mullion is to just slide over the sleeve and have a 10mm gap between the lower mullion. No welding is permitted. My question is that how can i consider this assembly of mullions as continuous. Is bolting of upper mullion to the sleeve a must? What length of the sleeve should i propose? Should i rather put the sleeve at the point of inflexion?


thanks
 
Replies continue below

Recommended for you

Sleeve is located at point of inflection. It is necessary to have the sliding capability since the floor deflect at differnet magnitude, and aluminum has large coefficient of thermal expansion.
 