ryholde
Structural
- Oct 6, 2014
- 4
I am working on an old masonry building where the wood joists are pocketed into the masonry wall. I have several joists that are rotten at the bearing points. The joist are simple span 15'-9" from wall to wall and are uniformly top loaded by a roof top terrace. The joists have approximately 3" of bearing in the wall pocket. I am proposing the following repair.
1) remove the old damaged joist.
2) Install a new 2x wood joist into the pocket in each wall with a splice located at mid span so the joists can be slid into the wall pockets.
3) Sister a new 2x member to each side of the spliced member. The sisters would be approximately 1" shorter than full span.
I have already verified that the single 2x wood member bearing on the wall can resist the shear and compression perpendicular to grain. The (2)-2x sister members are sufficient to resist the applied moment and meet deflection requirements. I plan on designing a cluster of nails near the end of the (2)-2x sister members to transfer the shear from the sister members back into the single 2x member that bears in the masonry pocket.
My question is what forces should the splice at mid span be designed for. I do not need the spliced member to resist the moment at mid span but the assembled member has a hinge at this point that needs to be stabilized. I had this conversation with another engineer in our office and we had different answers to the problem. I attached a sketch of each proposed solution. I would appreciate any input.
1) remove the old damaged joist.
2) Install a new 2x wood joist into the pocket in each wall with a splice located at mid span so the joists can be slid into the wall pockets.
3) Sister a new 2x member to each side of the spliced member. The sisters would be approximately 1" shorter than full span.
I have already verified that the single 2x wood member bearing on the wall can resist the shear and compression perpendicular to grain. The (2)-2x sister members are sufficient to resist the applied moment and meet deflection requirements. I plan on designing a cluster of nails near the end of the (2)-2x sister members to transfer the shear from the sister members back into the single 2x member that bears in the masonry pocket.
My question is what forces should the splice at mid span be designed for. I do not need the spliced member to resist the moment at mid span but the assembled member has a hinge at this point that needs to be stabilized. I had this conversation with another engineer in our office and we had different answers to the problem. I attached a sketch of each proposed solution. I would appreciate any input.