Spray Booths

Status
Not open for further replies.

MitchellCons

Mechanical
Oct 4, 2008
10
I have a question, are sprinklers always required at the top of the exhaust duct out the top of a spray booth or can we install a sprinkler just over the fan motor if the motor sits right on top of the booth itself? Everything I find in NFPA 13 leads me to believe that sprinklers are always required at the top. But I have personly seen designs and installations that provide sprinklers over the fan motor only when the motor is on the top of the booth and not @
the roof.

Thanks for your help in advance
Brent

 
Replies continue below

Recommended for you

may be a nfpa something thing saw it required once, but been to long cannot remember where the requirement came from.


also do not have a fire code in front of me, anything in there???
 
Thanks for the response. Sorry I think I started 2 of the same threads. Maybe someone can fix that for me. I would really like to know where NFPA states only a sprinkler @ the fan moter would be acceptable but I might be looking for something that is non exsistant. I also dont have the fire code near by and was wondering if the information I am looking for is there as well.

Thanks for all you help.
 
As per NFPA 33, 2007 edition

9.1* General.

Spray areas, which include by definition any associated exhaust plenums and exhaust ductwork, any particulate filters, any solvent concentrator units, any recirculation air supply units, and mixing rooms, shall be protected with an approved automatic fire protection system.


9.4.5 The sprinkler system shall be controlled by a separate, listed indicating valve(s), operable from floor level.

9.4.6* Sprinkler systems protecting stacks or ducts shall meet all of the following requirements:

(1) Sprinklers shall be spaced no more than 3.7 m (12 ft) apart.

(2) If exhaust ducts are manifolded, a sprinkler shall be located in the manifold at the junction of each exhaust duct with the manifold.

(3) Sprinklers shall provide a minimum flow of 114 L/min (30 gpm) per head at a minimum of 1 bar (15 psi) pressure.

(4) Sprinklers shall be ordinary temperature rated, unless required to be higher due to operating temperatures measured in the ducts, in which case the operating temperature shall be at least 28°C (50°F) above the inside temperature of the duct.

9.4.6.1 Stacks and exhaust ducts shall be provided with access openings for inspection and cleaning of sprinklers.

9.4.6.2 Sprinkler systems protecting stacks and ducts that are subject to freezing shall be of a nonfreezing type or be a manually controlled open-head system.

9.4.7 Sprinklers shall be protected against overspray residue, either by location or covering, so that they will operate quickly in event of fire.

9.4.7.1 Sprinklers shall be permitted to be covered only by cellophane bags having a thickness of 0.08 mm (0.003 in.) or less or by thin paper bags. These coverings shall be replaced frequently so that heavy deposits of residue do not accumulate.

9.4.7.2 Sprinklers that have been painted or coated by overspray or residues shall be replaced with new sprinklers.



****************************************
Fire Sprinklers Save Firefighters’ Lives Too!


 
I don't think NFPA 13 calls for liqued-tight fittings in the duct, but that would be a good spec to add. Liqued-tight fittings are available in 3/8" to 1" pipe sizes. Access panels are also a good idea. I do not know of any UL listed panels for paint booths, but they are available for grease ducts and exhaust hoods used in commercial kitchens.
 