I am finishing a single story precast project at a site where the geotech has indicated the spread footings must be tied in two directions per the clause below. I do not agree with that assertion based on the site parameters, but I have given up debating with the Geotech. In the past we have detailed a footing between each pad footing, but in this case I am being asked to encase the ties in the floor slab (slab on grade) like they did at the first bldg built on the site (diff eng). The bays are not large in this building, so the tie force is only 15kip. The problem I have with this is the fact the continuous ties will restrain the slab shrinkage during curing. My question is would you be concerned with this to the point you would not permit this solution, or what measures would help to minimize cracking during the cure?

The geotech has also completed a lengthy study into the potential for liquefaction at the site. They have recommended quite a large differential settlement across the width of the bldg. I was asked to design the foundation similar to the first building where typical spread footings are used. I am sure the building will stand up for the occupants to escape during the worst case seismic event in the report, but I expect the bldg will be a write off. This foundation type is very common for this budling size and location, but I believe one could reduce the overall risk with a different foundation type if they wanted to spend the $$. My question is, do most send a letter to the owner discussing this or do you consider the fact the owner has the geotech report sufficient?

TIE-Q_wwxlan.png


diff_settlement_lj85k9.png
 
Replies continue below

Recommended for you

You could wrap the ties with a bond break if it is a concern, although I would imagine cracking is still going to happen at the construction joints.
 
Thks canwesteng. The consensus was I am being a bit pedantic. I will add a construction joint and move on.
 
Whoops, think I meant contraction joint - too early for me.
 
If it is in a liquefaction zone (Richmond? Delta?) usually you see raft foundations instead of conventional footing systems. However, sometimes a footing is what is needed. In that case, yes, I would at least notify the owner that there are other foundation types they can explore. This would at least cover you for "duty to report" IMHO.

Although liquefaction ain't no joke, I do believe that anyone building in a liquefiable area knows what they are getting into. Seismic design doesn't mean "no damage" it means "limit the damage so everyone can get out of the building". It would be extremely cost prohibitive (in most cases) to design a normal importance building in such a way that any or all damage from a seismic event is negligible.
 
This is in Pemberton. Sa(0.2)=0.355. I had a discussion with the architect and he understood the limitation. He was not sure what the owner understood. I will have a chat with them at some point. Thks skeletron.
 