Sprinkler Design for Generator Room

Status
Not open for further replies.

rigal357

Specifier/Regulator
Sep 9, 2015
1
thread184-288042
stookeyfpe (Specifier/Regulator)15 Dec 10 14:31
It depends on the arrangement of the fuel tanks and fuel oil piping systems. If all liquid supply and withdrawl connections are at the top of the tank, I have accepted OH2. If piping is below the tank's liquid level I would specify a minimum EH1.


Stookeyfpe, where does this information in regards to the location of the piping determining the hazard to be utilized comes from? I have looked all over NFPA, and have not found it. Could you point me in the right direction please.

Thanks, Rigal357
 
Replies continue below

Recommended for you

Read the thread in its entirety. The answer is stated.
 