I'm trying to develop a cookie cutter criteria for dictating when to change the sprinkler head k-factor. Maybe, it's not possible to have a fixed plan for this, but I thought I'd throw this out to the community to see what you think.
I'm designing a system that is Ordinary Hazard Group II. I'm using Quick Response sprinkler heads and am able to reduce the remote area by 38% [NFPA 2007 11.2.3.2.3.1]. So, I'm dealing with 0.20 gpm/ft^2. The minimum pressure per head is 7 psi. My coverage per head is 127.5 ft^2. So, flow (Q) is 25.5 gpm (Q = δ * Area) out of the most remote head. Using a 5.6 k-factor head, this yields a pressure of 20.74 psi (Q = k * p ^(1/2)). Flowing 8 heads in this scenario. This system is fed from an existing pump (1500 gpm @ 100 psi) and I'm well under the curve (38.5 psi below the curve). I could use these heads and feel fully confident they would function to protect this space.
However, if I go up to an 8.0 k-factor head, the minimum end head pressure drops to 10.2 psi. This results in 44.7 psi below the curve. 8.0 k-factor heads are more expensive, though. So, what are the criteria that dictate when to raise k-factor. Is the thought process just "as long as I'm at least 10% under the curve, I'm fine"?
I'm designing a system that is Ordinary Hazard Group II. I'm using Quick Response sprinkler heads and am able to reduce the remote area by 38% [NFPA 2007 11.2.3.2.3.1]. So, I'm dealing with 0.20 gpm/ft^2. The minimum pressure per head is 7 psi. My coverage per head is 127.5 ft^2. So, flow (Q) is 25.5 gpm (Q = δ * Area) out of the most remote head. Using a 5.6 k-factor head, this yields a pressure of 20.74 psi (Q = k * p ^(1/2)). Flowing 8 heads in this scenario. This system is fed from an existing pump (1500 gpm @ 100 psi) and I'm well under the curve (38.5 psi below the curve). I could use these heads and feel fully confident they would function to protect this space.
However, if I go up to an 8.0 k-factor head, the minimum end head pressure drops to 10.2 psi. This results in 44.7 psi below the curve. 8.0 k-factor heads are more expensive, though. So, what are the criteria that dictate when to raise k-factor. Is the thought process just "as long as I'm at least 10% under the curve, I'm fine"?