When designing sprinkler head locations, our FP Engineer locates the heads to protrude through a suspended ceiling tile, so all are essentially on the underside of the suspended ceiling. No sprinkler heads are located above the suspended ceiling which is used as an air plenum for return air back to the air handlers (no return ductwork, just registers in the tile). There are no combustibles above the suspended ceiling, which is why the FP Engineer says none are required above the suspended ceiling.
There is a data center installation, where there will be a tremendous amount of heat load and thus many, many return air registers in a similar orientation as mentioned above. The ceiling registers will amount to be approximately 1/3 of the total suspended ceiling.
The FP Engineer is considering adding sprinkler heads above the suspended ceiling, on the underside of the ceiling above. He is worried that heat will zip past the heads below the suspended ceiling and not be detected.
It wouldn't be too much of a a problem, except it is a pre-action system, which would mean detection would be required above the suspended ceiling too, which would have to be accessed every year for testing (clear for smoke entry).
What are your thoughts for this requirement?
I think there is so much air flow in a data center environment, that the sprinkler system will only operate in a "real" serious fire, or if the air flow is shut down anyway.
There is a data center installation, where there will be a tremendous amount of heat load and thus many, many return air registers in a similar orientation as mentioned above. The ceiling registers will amount to be approximately 1/3 of the total suspended ceiling.
The FP Engineer is considering adding sprinkler heads above the suspended ceiling, on the underside of the ceiling above. He is worried that heat will zip past the heads below the suspended ceiling and not be detected.
It wouldn't be too much of a a problem, except it is a pre-action system, which would mean detection would be required above the suspended ceiling too, which would have to be accessed every year for testing (clear for smoke entry).
What are your thoughts for this requirement?
I think there is so much air flow in a data center environment, that the sprinkler system will only operate in a "real" serious fire, or if the air flow is shut down anyway.