Atari707
Computer
- Feb 24, 2013
- 3
Hello Eng-Tips,
I have a commercial (retail) space that has fire sprinklers installed.
I have an area with a standard 100amp circuit breaker panel, a small security alarm panel (DSC PC1832), and a light switch that I have enclosed to keep customers from disturbing this equipment (Children had a habit of flipping the light switch on/off) :]. So this is now enclosed in approx 4'W x 2'D x 7' H closet. The closet has a door, and the ceiling of this closet does not connect with the ceiling of the outside space.
Assuming combustibles are forbidden to be stored in this room, would NFPA code require me to add s sprinkler inside this area?
If yes, would removing the drywall making up the ceiling of the room change anything in that regard? This would effectively make it a framed & dry-walled partition and the nearest sprinkler would then be able to reach inside the partitioned area.
Thanks,
I have a commercial (retail) space that has fire sprinklers installed.
I have an area with a standard 100amp circuit breaker panel, a small security alarm panel (DSC PC1832), and a light switch that I have enclosed to keep customers from disturbing this equipment (Children had a habit of flipping the light switch on/off) :]. So this is now enclosed in approx 4'W x 2'D x 7' H closet. The closet has a door, and the ceiling of this closet does not connect with the ceiling of the outside space.
Assuming combustibles are forbidden to be stored in this room, would NFPA code require me to add s sprinkler inside this area?
If yes, would removing the drywall making up the ceiling of the room change anything in that regard? This would effectively make it a framed & dry-walled partition and the nearest sprinkler would then be able to reach inside the partitioned area.
Thanks,