bobinillinois
Mechanical
- Feb 22, 2011
- 12
As many of you are no doubt aware, effective 8/13/2013, long term care facilities that receive any type of Medicare/Medicaid funding will have to be compliant with Federal Register mandate 73 FR 47075.
"This regulation requires all long term care facilities (Skilled Nursing Facilities/Nursing Facilities) to be equipped with a supervised automatic sprinkler system by August 13, 2013, installed in accordance with the 1999 edition of the National Fire Protection Association's (NFPA) "Standard for the Installation of Sprinkler Systems" (NFPA 13)."
"This includes for example, the requirements for closets, walk in coolers/freezers, overhangs, loading docks and shafts to have sprinkler coverage."
All installation work is expected to be completed by August 13, 2013, as there are no provisions in the regulation to extend the timeframe for regulatory compliance beyond August 13, 2013, either through waivers of the use of the FSES."
I'm interpreting this to mean that all of these facilities must be fully sprinkled, with BFP's.
My question is will this also mean that quick response heads must be used everywhere?
The 1999 edition of NFPA 13 5-3.1.5 states, Sprinklers in light hazard occupancies shall be the quick-response type as defined in 1-4.5.2.
But Exception No. 2 says For modifications or additions to existing systems equipped with standard response sprinklers, standard response sprinklers shall be permitted to be used.
Exception No. 3 goes on to say, When individual standard response sprinklers are replaced in existing systems, standard response sprinklers shall be permitted to be used.
So will everybody have to use quick response heads or not?
Your feedback is greatly appreciated.
"This regulation requires all long term care facilities (Skilled Nursing Facilities/Nursing Facilities) to be equipped with a supervised automatic sprinkler system by August 13, 2013, installed in accordance with the 1999 edition of the National Fire Protection Association's (NFPA) "Standard for the Installation of Sprinkler Systems" (NFPA 13)."
"This includes for example, the requirements for closets, walk in coolers/freezers, overhangs, loading docks and shafts to have sprinkler coverage."
All installation work is expected to be completed by August 13, 2013, as there are no provisions in the regulation to extend the timeframe for regulatory compliance beyond August 13, 2013, either through waivers of the use of the FSES."
I'm interpreting this to mean that all of these facilities must be fully sprinkled, with BFP's.
My question is will this also mean that quick response heads must be used everywhere?
The 1999 edition of NFPA 13 5-3.1.5 states, Sprinklers in light hazard occupancies shall be the quick-response type as defined in 1-4.5.2.
But Exception No. 2 says For modifications or additions to existing systems equipped with standard response sprinklers, standard response sprinklers shall be permitted to be used.
Exception No. 3 goes on to say, When individual standard response sprinklers are replaced in existing systems, standard response sprinklers shall be permitted to be used.
So will everybody have to use quick response heads or not?
Your feedback is greatly appreciated.