Can someone tell me if this is over spaced for 130 sqft maximum sprinkler spacing? This is a freezer compartment.
If so is there anyway we can use this layout per code like EC sprinklers? Thanks
 
Replies continue below

Recommended for you

It looks like you are 14'-1 x 11'-4". I would say that is over spaced for 130 sq ft. There are dry ex cov sprinklers, but you have to meet all of the criteria for the obstructions. Depending on how deep your evap coolers are, you may not make it. I am not sure if those dry ex cov sprinklers are QR, so that may present a problem if you need everything QR.