haze10
Electrical
- Jan 13, 2006
- 81
We are doing a Group replacement of all the sprinkler heads in our boiler room and machine room. The original design from the 1960's has 286F heads in both spaces. Check the 2010 NFPA code in Chapter 13, Table 6.2.5.1 says that ceiling temps up to 150F should be 'Intermediate' with max sprinkler temp of 225F, and ceiling temps up to 225F should be 'High' with max sprinkler temp of 300F.
The boiler room and machine room at the ceiling would typically be less than 150F - the Boiler room might hit 130F and the machine space might hit 110F. So my thought is to go with 225F Intermediate heads.
My coworker thinks the 286F heads might have been spec'd to deal with steam leaks or upsets in the space that raised the room temperature.
What are you normally specifying for sprinkler temp inside boiler rooms and are relatively modern and adequately ventilated.
The boiler room and machine room at the ceiling would typically be less than 150F - the Boiler room might hit 130F and the machine space might hit 110F. So my thought is to go with 225F Intermediate heads.
My coworker thinks the 286F heads might have been spec'd to deal with steam leaks or upsets in the space that raised the room temperature.
What are you normally specifying for sprinkler temp inside boiler rooms and are relatively modern and adequately ventilated.