Sprinklers under underside of OPEN stair run??

Status
Not open for further replies.

av610

Mechanical
Dec 17, 2013
2
I was wondering what kind of protection is needed for the underside of the stairway (attached) if any? The stair run is 4'=6" wide.

Thanks
 
Replies continue below

Recommended for you

Normally see run down the slope of the escalator

Spaced to cover area under the escalator

Do you also have to provide opening protection ???
 
I saw that post and is helpful for the Vertical Opening aspect. However, I am still trying to determine if any protection is needed on the UNDERSIDE of the stair way since it is not enclosed.

The first stair landing is at ~6'-10" while the top of the stair will hit the next level at 16'-0"

Here are some pictures i found on google:

thanks.
 
Yes required obstruction of overhead sprinklers
Over four feet wide
 
8.5.5.3* Obstructions that Prevent Sprinkler Discharge from Reaching Hazard. Continuous or noncontinuous obstructions that interrupt the water discharge in a horizontal plane more than 18 in. (457 mm) below the sprinkler deflector in a manner to limit the distribution from reaching the protected hazard shall comply with 8.5.5.3.


8.5.5.3.1* Sprinklers shall be installed under fixed obstructions over 4 ft (1.2 m) wide.
 