I am the structural engineer for the job and this is the first time that stack bond has come up on a job for me. The architect has specified stack bond for aesthetics.
I have some pretty high walls and I am concered about the behavior of the stack bond under wind load. I can't justify in my head that if I have vertical bars at say, 48"o.c., that the lateral load on the un-reinforced portions of the wall will transfer to the reinforced cells across the continuous head joints.
Everything I read says that you should think of stack bond as 16" vertical pilasters with a vertical joint on each side of the blocks. If this is the case, how does the lateral load get to the grouted, reinforced cells? It seems to me that you would have to have a vertical bar in each block. If you count on the joint reinforcement to transfer the load then I would need to specify truss type joint reinforcement, right? Because the ladder type would be unstable for load normal to the wall.
Also, I was under the impression that the vertical bars required on each side of a normal vertical control joint in cmu walls was required for the very reason I mentioned above. If this is the case and you assume a control joint on each side of each block in stack bond, then wouldn't the same requirement hold true?