stack effect

Status
Not open for further replies.

struct_eeyore

Structural
Feb 21, 2017
264
Hi all,

Not a fluid engineer, so forgive my ignorance. I'm hoping someone can direct my to the proper way to calculate air flow rate in a open ended stack. Stack is 100' high, bottom is about 10' away from ground surface, 10' in diameter; a 6 ft/sec wind is blowing across the top. Temperature differential is negligible.
 
Replies continue below

Recommended for you

Flow through this stack can only be due to this "negligible temp difference". Run the calcs for say 1-2degC delta T and see what flow you get. Delta T may be higher is summer when ground temps are warmer. For example, for ground temp at 27degC and a delta T of 2degC, I get 150kg/hr through the 10inch stack (exit velocity 0.75m/sec).
 