Mazzman
Geotechnical
- Aug 3, 2004
- 23
I received a copy of a subsurface exploration report prepared a licensed engineer with geotechnical experience. The project is a 8000-square-foot, wood-frame commercial building, and the work was conducted for a local developer.
The report states that the field sampling was done using a Giddings ATV rig. Apparently, this is a small pull-behind trailer with a power auger mounted on it (see attached photo from Giddings website). I'm told the engineer runs solid stem augers and conducts the field work himself.
No Standard Penetration Tests are conducted; however, the report of geotechnical exploration reports “Estimated N-Value” on the boring logs.
The logs in the report include “Cohesive Strength (psf)” values. The engineer told me he runs the augers down, and then lifts the augers exposing some soil within the auger flights. He then uses a hand-held penetrometer on the soil exposed on the augers to measure strength. He says the value he reports is equivalent to undrained shear strength.
I asked how he gets N-values if he does not run the SPT. He said the “Estimated N-Value” reported on the boring logs is based on some correlation he has between hand-held penetrometer value and Standard Penetration Test value.
The logs include USCS classification, but there is no indication in the report that soil classification tests, or any tests, for that matter, are conducted.
There are statements in the report that do not seem to be supported by data:
The report states “Penetrometer tests were performed on representative soil samples to evaluate soil shear strength, compressibility and consistency in-situ”. Based on the description of the field testing, it does not appear the sampling was conducted in-situ. Also, hand held penetrometers are not usually considered useful to predict compressibility.
The report says “This report…has been prepared in accordance with generally accepted geotechnical engineering practices.”
My question to you: Are the practices I've described here consistent with local geotechnical engineering practice for a similar project in your area?.
The report states that the field sampling was done using a Giddings ATV rig. Apparently, this is a small pull-behind trailer with a power auger mounted on it (see attached photo from Giddings website). I'm told the engineer runs solid stem augers and conducts the field work himself.
No Standard Penetration Tests are conducted; however, the report of geotechnical exploration reports “Estimated N-Value” on the boring logs.
The logs in the report include “Cohesive Strength (psf)” values. The engineer told me he runs the augers down, and then lifts the augers exposing some soil within the auger flights. He then uses a hand-held penetrometer on the soil exposed on the augers to measure strength. He says the value he reports is equivalent to undrained shear strength.
I asked how he gets N-values if he does not run the SPT. He said the “Estimated N-Value” reported on the boring logs is based on some correlation he has between hand-held penetrometer value and Standard Penetration Test value.
The logs include USCS classification, but there is no indication in the report that soil classification tests, or any tests, for that matter, are conducted.
There are statements in the report that do not seem to be supported by data:
The report states “Penetrometer tests were performed on representative soil samples to evaluate soil shear strength, compressibility and consistency in-situ”. Based on the description of the field testing, it does not appear the sampling was conducted in-situ. Also, hand held penetrometers are not usually considered useful to predict compressibility.
The report says “This report…has been prepared in accordance with generally accepted geotechnical engineering practices.”
My question to you: Are the practices I've described here consistent with local geotechnical engineering practice for a similar project in your area?.