1000kW, 400V standby generator was connected wrongly when first switched on. Red phase was connected to the LV Switchboard Neutral which is earthed and the neutral was connected to the Red phase bar. The load was not connected.
It appears the generator initially took a load of around 1mW, this then subsided to 500kW and then
down to 200kW, this is within a time period of around 10 seconds.
Initially a loud buzzing/ vibrating noise could be heard from the switchgear panel, this then seemed to lessen and then the generator breaker was opened. Not of the protection detected the fault.
I am a bit puzzled by the low value of the fault current. I would have expected a current of 3 x generator rating.
It seems that the current passed through the electrical equipment which cause a burning smell in the building.
Has anyone come across similar problem? I am wodering why the fault level is so low.