i am a little green with regard to the motors and the connection required to work them efficiently and correctly. I had a question to my supplier as to why the motor they supplied me was wired star as opposed to delta.
I got this reply from my questions. Can anyone eleborate as to why 63 frame up to 112 frame is 230v – Delta and 400v – Star. Above this frame size the voltage then is 400v – Delta and 690v – Star?
Sorry for the large amount of text but its best to give the whole picture!!
ME
Another question regarding the 3 motors now for the pumps you supplied to us on this order. The windings were in star or wye configuration. For this application can you confirm why these weren’t delta? Just out of interest as they work (well ones been tested so far) fine
SUPPLIER
Working against your PO 16917 these motors would be 230v Delta or 415v in Star.
ME
Can you confirm why these were 415V Star and not Delta then.
SUPPLIER
Why, did you want 415 Delta? 415v Delta in this frame size would be a special voltage, and need to be rewound specially.
ME
Having only dealt briefly with motor windings (usually I just like the plug it in and play in a complete system!) the question has been posed by the customer and I was hoping you would justify the star configuration for me with some technical justification/information to back it up.
SUPPLIER
The standard is 63 frame up to 112 frame is 230v – Delta and 400v – Star. Above this frame size the voltage then is 400v – Delta and 690v – Star.
This is due to the kW of the motors and the power required to run them.
The only real contentious issue is that some motor suppliers make the voltage change on 100/112 frame sizes, others 132 and a few 160 frames.
As you motors were 63 framed this is at the lowest end possible.
More the question, what voltage did you want to run them in?
ME
415V was the voltage we are running them on.
So the star or delta connection choice is done from the frame size?
SUPPLIER
Yes, and frame size is determined by power and speed, i.e. the larger kW of the motor the larger the frame.
So guys
Thanks for any help received! Laymans terms reply please LOL
Johnny H-S BSc(Hons) MInstMC
Engineers like to solve problems. If there are no problems handily available, they will create their own problems.
i am a little green with regard to the motors and the connection required to work them efficiently and correctly. I had a question to my supplier as to why the motor they supplied me was wired star as opposed to delta.
I got this reply from my questions. Can anyone eleborate as to why 63 frame up to 112 frame is 230v – Delta and 400v – Star. Above this frame size the voltage then is 400v – Delta and 690v – Star?
Sorry for the large amount of text but its best to give the whole picture!!
ME
Another question regarding the 3 motors now for the pumps you supplied to us on this order. The windings were in star or wye configuration. For this application can you confirm why these weren’t delta? Just out of interest as they work (well ones been tested so far) fine
SUPPLIER
Working against your PO 16917 these motors would be 230v Delta or 415v in Star.
ME
Can you confirm why these were 415V Star and not Delta then.
SUPPLIER
Why, did you want 415 Delta? 415v Delta in this frame size would be a special voltage, and need to be rewound specially.
ME
Having only dealt briefly with motor windings (usually I just like the plug it in and play in a complete system!) the question has been posed by the customer and I was hoping you would justify the star configuration for me with some technical justification/information to back it up.
SUPPLIER
The standard is 63 frame up to 112 frame is 230v – Delta and 400v – Star. Above this frame size the voltage then is 400v – Delta and 690v – Star.
This is due to the kW of the motors and the power required to run them.
The only real contentious issue is that some motor suppliers make the voltage change on 100/112 frame sizes, others 132 and a few 160 frames.
As you motors were 63 framed this is at the lowest end possible.
More the question, what voltage did you want to run them in?
ME
415V was the voltage we are running them on.
So the star or delta connection choice is done from the frame size?
SUPPLIER
Yes, and frame size is determined by power and speed, i.e. the larger kW of the motor the larger the frame.
So guys
Thanks for any help received! Laymans terms reply please LOL
Johnny H-S BSc(Hons) MInstMC