star point

Status
Not open for further replies.

vavavoom

Electrical
Aug 26, 2005
1
my boss has just informed me that if the earth( ground) is connected to star point it will potentially become live is this true

 
Replies continue below

Recommended for you

Live Earth? That would be a new one; ground (earth) is the reference voltage, anything solidly connected to ground is at zero volts. If there is current flow in the connection, there will be a voltage drop between the point measured and ground, but ground is still at zero.
 
Connecting the starpoint of a transformer, generator et.c. to ground is giving you a TN- or TT- system (the first T means solidly grounded neutralpoint). The other letter is determining how your PE-conductor goes.

If the neutral is not connected to ground, you would have a floating neutral, i.e. an IT-system.

:)

tm
 
Aside: 'T' comes from the Latin word for 'earth', Terra.


----------------------------------

One day my ship will come in.
But with my luck, I'll be at the airport!
 
Astute point ScottyUK! I was just thinking why "T"!?!?

You are clairvoyant.[spin]
 