jfrye
Mechanical
- Aug 18, 2015
- 4
I have two centrifugal 3HP single phase submersible sewage pumps, which use 2 start caps (rated 72-86µF) wired in parallel and 2 run caps (55µF) wired in series to operate. These pumps have been failing out due to overtemp during high flow conditions, so "continuous" running. I believe I need to choke the supply voltage down; the mfr says that when continuously running the voltage variation should be ±5% of 230VAC, line to line the supply is 251VAC which is greater than +5%.
That said, there is still another mystery to me with the start caps, as I said before they are labeled 72-86µF, but when metered with a multi-meter set for capacitance they all read ~130µF, this is with all the wiring removed, there is only a discharge resistor(which is soldered on) attached to the start cap terminals. I personally installed the new capacitor kits a month or two ago, and checked everything which at the time was nameplate normal. So has anyone ever seen the capacitance of a capacitor change and not explode?
That said, there is still another mystery to me with the start caps, as I said before they are labeled 72-86µF, but when metered with a multi-meter set for capacitance they all read ~130µF, this is with all the wiring removed, there is only a discharge resistor(which is soldered on) attached to the start cap terminals. I personally installed the new capacitor kits a month or two ago, and checked everything which at the time was nameplate normal. So has anyone ever seen the capacitance of a capacitor change and not explode?