Starting a 4500 hp motor while it was coasting down 2
  • Thread starter Thread starter -
  • Start date Start date
Guest
I work in a refinery. We recently inadvertently tripped a 12 kV circuit. The 12kV circuit was reclosed within 30 seconds. One of the loads on that circuit is a 4500 hp motor that is a driver for an air compressor. The motor has a breaker for a starter. The motor's breaker never opened during the outage. Its trip/close power is from the substation. Thus, one of the loads that was picked up as soon as the breaker was reclosed was the 4500 hp motor. When the tripped circuit was re-energized the motor was still coasting down. The motor's normallly runs at 1800 rpm. At the time the breaker was closed it had coasted down to 450 rpm. My questions are, should I change the motor control circuit so that upon loss of main power to the motor to trip the motor? If so/or not so why?
I don't understand how you can have ANY damage if there is no electrical phase problem. Why would a coasting start even be AS hard on a motor system then a full start? Isn't the back emf going to automatically limit the rotor heating and inrush? Why would there be one iota of "key shearing"? I would think any motor would be delighted to have a running start. I would think you could have 100 restarts an hour that are 20 cycles from the power loss.
AS LONG AS THERE IS NO RESIDUAL VOLTAGE. Would someone please explain why this would be wrong.
The only issue that I am aware of on restarting a rotating motor, is the interatcion of the supply voltage and the generated voltage of the motor. Provided that the generated voltage from the motor is insignificant, then there is no problem restarting a rotating motor. (except on a VFD!)
Typically, the voltage generated by the motor will decay in less than 1 second, it is a function of the rotor time constant and this varies from motor to motor. I expec that the new "High Eff" motors will have a longer time constant due to the lower rotor resistance.
Best regards,
Mark Empson
Yes, but it is still a very short time, maybe 2 seconds at most?
horsedragon,
You appear to be new, welcome to the forum. You were most likely unaware of the guidelines but just so you know, it is generally considered inappropriate to resurrect threads older than 6 months. What you can do if interested in discussing an issue like this is to start a new thread, then in your first message, reference the old thread by copying and pasting the "thread ID number" at the top of the page. This helps to avoid confusion.
For example, I can reference another similar thread on transition spike damage by finding that thread in another browser window, then copying and pasting that thread ID number into this message like this thread237-42958 . If you notice, it is highlighted and is a link to that old thread imbedded into this one. Now all the information from that old thread is readilly available for reference without cloggin up the new thread with old posts.
There are more tricks and guidlines available at the FAQ listed at the end of my signature line.
Again, welcome to the forum and enjoy!
"Our virtues and our failings are inseparable, like force and matter. When they separate, man is no more." Nikola Tesla
Read the Eng-Tips Site Policies at faq731-376
[pirate]Member, [blue]P3[/blue]