jwilson3
Electrical
- Dec 20, 2001
- 45
I'm in a disagreement with an Engineer with a major electrical equipment manufacturer over the basics of a thyristor controlled soft starter. I am trying to calculate the voltage drop profile on the supply system during starting.
The Engineer's analysis shows the initial starting voltage at 30% and the motor current at 330A with 20%PF and ramps up to 598A as the voltage is raised. That's the range of current values I say needs to be used in the voltage drop calc. The Engineer says the current to use is the current on the source side of the starter, which would be 30% of the current on the motor side at start and would rise to equal the motor side current as the voltage is ramped up.
I say he's wrong, that the current is virtually the same on either side of the starter.
The Engineer's analysis shows the initial starting voltage at 30% and the motor current at 330A with 20%PF and ramps up to 598A as the voltage is raised. That's the range of current values I say needs to be used in the voltage drop calc. The Engineer says the current to use is the current on the source side of the starter, which would be 30% of the current on the motor side at start and would rise to equal the motor side current as the voltage is ramped up.
I say he's wrong, that the current is virtually the same on either side of the starter.