Hi,
My explanation is as follows.
In fact the you should have indicated the HP(kW) and the motor name plate voltage rating and the type of the motor (Induction, Sync, DC etc) so that the discussion will be more realistic. Any how both IEC & NEMA allow +/- 10% of the motor rated voltage drop during steady state running and NEMA allows 15% drop at the motor terminals whereas IEC motors can have only down to 10% drop.
If I presume that the motor nameplate voltage to be 230 V, 3-phase ( a typical North American NEMA product) with D.O.L. starting.
Steady state : (+)10% of 230 V = 253 Volts & (-)10% of 230 V = 207 Volts.
If everything is fine and if this motor operates between 207 to 253 Volts, then it should deliver its nameplate power at the rated ambient temperature.
Starting: If we calculate the terminal voltage at the start, then we are allowed to go down to 85% of 230 V= 184 V. That means at the start, if the total inertia is within the stipulated limits, this motor should start without any trouble even at 184 V. But it should accelerate with in the given time.
Whether an ind/sync. motor is started at full load or no-load it DOESNOT affect the magnitude of the starting (locked rotor) current. It is always the same and it will be 6-8 times the motor name plate full load current (or given by the manufacturer or as per given in NEMA) The only change is in the accelerating time. When we start a pump with the discharge valve closed, then it will take a little shorter time than when it is started with open discharge valve. Finally, the motor will settle at no-load speed or the full load speed depending on the flow requirement. If we keep the discharge valve opening (number of turns) corresponding to the motor full load current and then start, after the starting inrush the motor current will settle down at full load reading. Typical example is a fire pump where we don’t want to manually throttle the discharge valve during a fire situation. Instead, the fire pump should deliver its full flow to the fire right from the start. But in a process plant what we do is, after the starting time, we manually (or by a DCS system ) throttle the discharge as per our flow requirement up to the full load of the motor. As a precaution we don’t keep the discharge valve tightly closed at the start because specially in large pumps it may lead to cavitation etc. So we used to “ crack open “ the discharge valve for about 50-60% through a “by-pass line”. Then the motor will start with 50-60% full load, but will not deliver fluid to the main system. After the starting we can throttle the main valve as per our flow requirement while slowly closing the by-pass valve.
Therefore there is no harm in starting a ind/sync. motor at full load, but we should make sure
1)during the prolonged starting time the over current protection should not unnecessary trip the motor.
2)minimum of 15% of the motor name plate voltage should be available at the motor
terminals during the start-up process.
3)during the steady state running, voltage available at the motor terminals should be between 207 & 253 Volts.
Regards!