Hi HenkV
After you received a lot of good info,I don't know if you have any better idea as to the cause of failure.
You still have another 5 motors being used .If the problem is a system problem (VFDs)rather than a motor pronblem, it could just as easy happened on any of the other motors.
When one hears of 1st coil,1st turn fault automaticaly we assume a Voltage spike from inverter use.
I just like to mention something that is a characteristic of most windings (Form or Random).When coils enter or leave slots, they can be stressed with a downword pressure that weakens the Millar slot insulation.At times this insulation is actually cracked under the coils.It is true that it happens much more on Random windings than on formed coil.I have seen formed coil windings that have shown the tell tale marks.When this happens,motors may pass most tests,with age,this weak spot will be the weak link.This may not be the case, and it is easy to look for this condition.
If your rootcause does not show a possible power problem,how do you plan to test the other motors to make sure they are sound ? Henkv, If you don't mind, give us an idea how do you plan to check the other drives.If you are going to test'em.
Thanks
GusD