There are two basic types of dual fluid atomising nozzles, whether it uses air or steam as the atomising medium.
1) Internal mix or 2) External mix.
Firstly Internal mix
Types of these are I-Jets and T-Jets
Requires quite a large proportion of steam or air to fuel. Typically 0.2lb to 0.3lb medium/ lb of fuel.
There is a common mixing chamber before the steam/ fuel or air/ fuel exits so the medium pressure must always be higher than the fuel pressure to prevent oil entering the atomising med. supply lines. This is typically kept 15-30psi above the oil pressure by some form of differential press control valve. Typical oil pressure would be 90psi, but can be higher or lower.
Here the steam pressure augments the lower oil pressure to assist with atomisation. In fact there are certain types which turn off the steam at higher fuel pressures when there is sufficient mechanical energy available with fuel pressure alone.
Atomisation is excellent with turndowns typically 8 or 10 to 1.
External mix.
The well known Y-Jet is of this type.
Requires less medium consumption 0.05lb to .07lb/ lb fuel.
Medium pressure does not have to be higher than fuel as the interaction is very "local" just before emission out of the nozzle. Supply of the fuel through drillings at an angle to the steam drillings causes the fuel to enter into the high velocity steam which efficiently "tears away" the fuel finely atomising it. There are a number of these drilling combinations terminating in common exit orifices(say 6 to 10 per nozzle).
Atomisation is slightly less efficient compared to the internal mix, but still excellent and capable of 10 to 1 turndowns.
As you can see there is mainly a mechanical effect, but having the steam mixed with the oil assists the effect by its expansion on exiting also "blowing the fuel apart"
The steam must be dry or the free water will cause pulsations in burner operation.
In all types of assisted atomisation the fuel pressure can be much lower than pure pressure atomisation and the viscosity of the fuel much less.
There is another type of atomising which uses this emulsification property. Here a metered quantity of WATER is fed into the heavy oil (up to 6% of the fuel). It must be well mixed and not come through as slugs. The nozzle is a pure pressure jet, but the effect of water turning to steam achieves the enhanced atomisation.
Hope this helps,
Rod Nissen.