steam flow formula

Status
Not open for further replies.

helpyou

Automotive
Sep 26, 2011
79
Hi

one DP flow transmitter is measuring steam flow. Operating temperature is changed/increased from original Temp (in datasheet). Should we do the recalculation and configure the transmitter ? Is temperature a factor in steam flow calculation ?

Thank you
 
Replies continue below

Recommended for you

No need to reconfigure the FT. Compensate for the reduced steam density by manual means to get the corrected steam mass flow or you can do this compensation online in the DCS if you have a TT nearby the FT - see flow measurement handbooks for temperature correction procedure.
 