grant464
Mechanical
- Jan 22, 2008
- 12
I have a 3-stage steam jet air ejector system that produces vacuum for a process. The two inter-condensers are direct contact, not surface.
The condensers currently operate on 75-80 F closed loop water. A big problem in the hot summer months is that our cooling tower cannot make water cold enough for the condensers. When the water temperature climbs to 90-95 F, we have to slow down the process significantly, or turn it off.
In theory, increasing the water flowrate through the condenser should allow us to operate at a higher water temperature (i.e. 90-95 F), since this is just a heat transfer problem. Does this hold true in practice, or are there other factors that need consideration?
I can also tell you, that the water inlet valves to the condensers are only 30% open right now. This is because the drain pipe was never sized correctly and water starts to back up into the condenser if the valve is opened too much. The maintenance guys found that 30% open gives the "best performance" with the current setup.
Also, the small amount of documentation I have on these VERY old condensers is: Maximum condensing water temperature 95 F.
I have ruled out purchasing a chiller to bring the water temperature down because of excessive cost! Our flow rates are in the order of 500 gpm.
Thanks for the discussion,
- Grant
The condensers currently operate on 75-80 F closed loop water. A big problem in the hot summer months is that our cooling tower cannot make water cold enough for the condensers. When the water temperature climbs to 90-95 F, we have to slow down the process significantly, or turn it off.
In theory, increasing the water flowrate through the condenser should allow us to operate at a higher water temperature (i.e. 90-95 F), since this is just a heat transfer problem. Does this hold true in practice, or are there other factors that need consideration?
I can also tell you, that the water inlet valves to the condensers are only 30% open right now. This is because the drain pipe was never sized correctly and water starts to back up into the condenser if the valve is opened too much. The maintenance guys found that 30% open gives the "best performance" with the current setup.
Also, the small amount of documentation I have on these VERY old condensers is: Maximum condensing water temperature 95 F.
I have ruled out purchasing a chiller to bring the water temperature down because of excessive cost! Our flow rates are in the order of 500 gpm.
Thanks for the discussion,
- Grant