Can someone point me to steam nozzle photo - not sure what it is? I'm sizing a 100HP 150 psi steam boiler for a process and the manufacturer recommends a 2-1/2" steam nozzle.

The boiler comes with a 4" flanged supply connection & thought I would use a 4" stop check & OSY valve. Is the nozzle a transition fitting?
 
Replies continue below

Recommended for you

Sounds like the mfr thinks that a 2½" outlet is big enough. Just use an Ecc. Reducer [flat on bottom] to go to your 4" header line.
 
I don't have a 4" header...just 1 boiler serving the process. The installation manual has a table that calls for the 2-1/2" nozzle.
 
You amy have the wrong manual. Assuminging that your 4" nozz is actually your steam outlet.

When speaking "boiler & pressure vessel", a nozzle is the flange [on a short neck] that sticks out from the shell of your boiler/vessel.
 