Anyone know where I can find a written reference from a creditable organization recommending steam relief valve discharge pipe sizing? I have a situation where a relief valve sized for 2,730 Lbs/hr at 25 psig lifted. The valve has a 2" inlet and 2-1/2" outlet. The valve discharges through a 2-1/2" pipe into a drip pan elbow. The drip pan elbow literature calls for a 3-1/2" or 4" discharge line.
Here's my problem, the installer put a 4x2 concentric reducer on top of the drip pan elbow and tied the relief line in to a 2" header. As I mentioned, the relief valve lifted and as you can imagine, I have a big mess of wet/melted insulation from steam blowing out the drip pan elbow atmospheric break.
So I know full well that a 4" line is required, but where can I find it in writing. I need some design specs in my arsenal to demonstrate that reducing to 2" was the cause of the problem.
Here's my problem, the installer put a 4x2 concentric reducer on top of the drip pan elbow and tied the relief line in to a 2" header. As I mentioned, the relief valve lifted and as you can imagine, I have a big mess of wet/melted insulation from steam blowing out the drip pan elbow atmospheric break.