It seems that customers can never give me this information. I am looking for a way to calculate it with higher confidence than I have.
Consider a tube and shell heat exchanger.
The shell gets steam from a pressurized, saturated steam source. The steam is controlled by a valve before it is released into the shell. Condensate is removed from the shell by a steam trap and the level remains below the tubes.
The tubes are filled with a fluid cooler than the steam. Obviously, I hope, the fluid comes in very cool, and leaves at a temperature somewhat warmer, but not as warm as the steam.
What is the pressure in the shell side of the heat exchanger? Does the condensate subcool to the temperature of the incoming fluid and does the pressure of the steam reflect saturation at the coolest temperature, or at the hottest temperature of the controlled fluid, Or is the shell pressurized to the suppy pressure of the steam and condensed at saturation temperature at that pressure?
This is more information that customers usually can give me, but they want me to calculate valve size for the steam supply valve. I get incomplete process conditions, but if it's wrong it's still "my fault". Energy balance is pretty easy to calculate. Delta-P across the valve is tough. Sometimes I just assume critical pressure drop, and go with that. I will be grateful for any insight.
Consider a tube and shell heat exchanger.
The shell gets steam from a pressurized, saturated steam source. The steam is controlled by a valve before it is released into the shell. Condensate is removed from the shell by a steam trap and the level remains below the tubes.
The tubes are filled with a fluid cooler than the steam. Obviously, I hope, the fluid comes in very cool, and leaves at a temperature somewhat warmer, but not as warm as the steam.
What is the pressure in the shell side of the heat exchanger? Does the condensate subcool to the temperature of the incoming fluid and does the pressure of the steam reflect saturation at the coolest temperature, or at the hottest temperature of the controlled fluid, Or is the shell pressurized to the suppy pressure of the steam and condensed at saturation temperature at that pressure?
This is more information that customers usually can give me, but they want me to calculate valve size for the steam supply valve. I get incomplete process conditions, but if it's wrong it's still "my fault". Energy balance is pretty easy to calculate. Delta-P across the valve is tough. Sometimes I just assume critical pressure drop, and go with that. I will be grateful for any insight.