A friend asked me to look at his home, currently under construction by a builder. One of those pick-your-floorplan type neighborhoods.
He showed me these photos of a steel beam supported by a single 2x6 stud in the basement (walkout basement). The other end of the beam is in a pocket in the concrete basement wall.
I would never support a beam like this. I always show pipe columns at all steel beams. The two other beams in his basement are supported by pipe columns.
I told him to have the builder add another stud or two and find or fab a bracket that can connect the steel beam to the 2x built-up post. The builder refused and said this was done per plans. I don't have access to the drawings, nor does my friend, to confirm. I doubt an engineer would show a single stud supporting a steel beam. And the rest of the house seems overbuilt anyway (triple 2x headers even in non-bearing walls, double trimmers, 2x6 walls throughout, thick plywood sheathing, etc). Doesn't seem like a skimpy engineer, especially for the type of development this is.
But... technically the stud can handle the load (I checked) and I can't seem to find a code provision in the IRC that says you can't do it.
I told my friend to just go and add the studs himself over the weekend but I'd love a code provision to toss at the builder. Any ideas? Located in Michigan, USA.
He showed me these photos of a steel beam supported by a single 2x6 stud in the basement (walkout basement). The other end of the beam is in a pocket in the concrete basement wall.
I would never support a beam like this. I always show pipe columns at all steel beams. The two other beams in his basement are supported by pipe columns.
I told him to have the builder add another stud or two and find or fab a bracket that can connect the steel beam to the 2x built-up post. The builder refused and said this was done per plans. I don't have access to the drawings, nor does my friend, to confirm. I doubt an engineer would show a single stud supporting a steel beam. And the rest of the house seems overbuilt anyway (triple 2x headers even in non-bearing walls, double trimmers, 2x6 walls throughout, thick plywood sheathing, etc). Doesn't seem like a skimpy engineer, especially for the type of development this is.
But... technically the stud can handle the load (I checked) and I can't seem to find a code provision in the IRC that says you can't do it.
I told my friend to just go and add the studs himself over the weekend but I'd love a code provision to toss at the builder. Any ideas? Located in Michigan, USA.