bgsmith
- Dec 12, 2007
- 25
I am engineering the anchorage of pre-manufactured steel columns to concrete slab/footings under the 2006 IBC. The reference to ACI 318-05 Appendix D notes that under moderate or higher seismic areas the steel failure must govern design. For uplift resistance I am having trouble meeting the code. Since the metal building company specifies anchor bolt number, size, and spacing I can't adjust the steel anchor capacity. Even with large embeddments and large footings I still cannot get the concrete breakout strength to exceed the steel strength. I am aware that the IBC also allows the anchorage to be designed as 2.5 times the actual loads instead of requiring the steel to govern. Increasing the load by 2.5 causes either the steel bolts to fail or makes it almost impossible to develop that much strength in concrete breakout. In the case of shear I have added hairpins to transfer the load into the concrete across the failure plane, but in tension I cannot develop the hairpins without creating very deep footings (more than 24"). The design is for a thickened slab edge with spread footings under columns. Any ideas? Thanks.