NAFTALI-HAKOHEN

Civil/Environmental
Apr 8, 2021
26
hi wondering how much of width of triangular plate takes the compression load from beam above, in corbel style connection
im designing:
Screenshot_2021-04-13_133346_d8fzle.jpg


Screenshot_2021-04-13_133654_mdpfd7.jpg


how wide is the design strip to take the compression?

and how do i calculate lateral compression length for a triangle like this- kind of laterally supported along its length?

thanks

naftali
 
Replies continue below

Recommended for you

Probably treat it similar to the bearing on a web format (10t+N) calculations.
 
A BS5950 book I have says 100mm is reasonable - and picks it out of thin air!
 
Why so many horizontal bolts? 28? seems a little overkill...

Rather than think climate change and the corona virus as science, think of it as the wrath of God. Feel any better?

-Dik
 
The closet similar thing I can think of is the stiffener plate in Bolted Extended End Plate Moment connections (see AISC Design Guide #4).

In that design guide examples, AISC does two checks on the stiffener:
1) Min thickness required for stiffener = thickness of beam web * (Fy_beam / Fy_stiffener)
2) b/t > 0.56*sqrt (E/Fy).... which is, I believe, based on the b/t slenderness limit for the flange of a wide flange under uniform compression.

If you follow those requirements, I believe the stiffener will not be subject to local buckling.
 