Steel deck diaphragm with all braces at interior

SocklessJ

Structural
Aug 24, 2017
45
- Single story building, 150'x200'
- Vertical system: Steel roof deck, bar joists, wide-flange girders, HSS Columns
- Lateral system: steel roof deck diaphragm, vertical braced frames (R=3)

With windows across the front wall, I planned to shift that line of bracing back a bay to avoid a 3-sided diaphragm. The architect then asked if I could move all bracing to interior walls to allow for horizontal expansion.

I tried this in ETABS using a semi-rigid diaphragm and drifts are low. Is there any reason not to go this route? Other than requiring more coordination every time they mess with those interior walls?
 
Replies continue below

Recommended for you

It's technically a cantilever so the deflection check probably is a bit funky or inaccurate in ETABS. I don't use that program much and never liked the non windows GUI anyhow.
 
I would probably run some hand calculations to confirm the diaphragm deflections, but I don't see an issue necessarily. What are your bay widths? 25'? so you'd have you braced core measuring 100'x150' and cantilevering 25' on each side? Proportions seem within range.
 
@lexpatrie
I agree with you on the ETABS GUI. I’m never quite sure if ive selected a member or not. It also crashes frequently. I’m a RAM elements fan myself but its not quite as powerful for building design.

@jayrod12
Good call. It’s always good to verify with a hand calc when trying something new.
 