Steel I-beam to Concrete Column Connection using A307 Bolts 2
SatoshiNakamoto09
25
Where can i get references about the minimum embeddment length required for A307 Bolts to connect Steel Beam to Concrete Column?
I'd take a look at ACIs provisions for anchorage (the old "Appendix D") and headed anchors, for a start.
just call me Lo.
ASIC's Design Guide #1 is also a good resource, particularly for more "rule of thumb" advice. Then, if your loads are anything but nominal, I'd back that up wit the ACI anchorage checks that Lomarandil mentioned.
Lomarandil or others;
Could you expand on your answer. Particularly on "Old" vs "New" (my add) Appendix D sections and on any sources that you feel explain these requirements well.
Jim
Old = provisions used to reside in Appendix D of ACI 318 in older version.
New = provisions reside in body of ACI 318 in latest versions.
jim said:
...and on any sources that you feel explain these requirements well.
Depends on how deep of a dive you want.
Shallow End: see attached Structuremag article.
Keeping up with the Jones': I'd just go straight to checking out Chapter 17 of ACI 318-14.
Mariannas Trench: Eligehausen. Pretty much the source material upon which AppD was developed.