I have been given a roof design to check that has 16K2 joists specified, but this design did not account for the placement of HVAC RTU's. I am now being contacted by the fabricator asking if we will be supplying loading diagrams for the joists that may be effected by the RTU's. The problem is that the RTU locations have not been set yet, as they keep changing with the architectural layout of the building. The options I see are as follows...
#1 Have the fabricator provide KCS joists in the "assumed" RTU locations so that the "actual" location does not effect design.
#2 Double-up (side to side) the joists at RTU locations so that the load carrying capacity at this location is doubled and tie the joists directly together via welding plates, etc...
#3 give the joist manufacturer an "assumed" loading diagram with and envelope of possible locations for the RTU's and have them design the joists for worst case within the envelope.
In the past, I have seen my company just have the joists doubled at the RTU locations, but I am not convinced that is the "right" thing to do, and being that I am new to this, I'd like to know the more correct thing to do. Showing KCS joists is the quickest fix but may be overkill? Diagrams are probably more "right" to give, but could be way off when it comes time for construction, especially with actual size and location of RTU not known.
Thoughts, suggestions???? I know this was a long post.
#1 Have the fabricator provide KCS joists in the "assumed" RTU locations so that the "actual" location does not effect design.
#2 Double-up (side to side) the joists at RTU locations so that the load carrying capacity at this location is doubled and tie the joists directly together via welding plates, etc...
#3 give the joist manufacturer an "assumed" loading diagram with and envelope of possible locations for the RTU's and have them design the joists for worst case within the envelope.
In the past, I have seen my company just have the joists doubled at the RTU locations, but I am not convinced that is the "right" thing to do, and being that I am new to this, I'd like to know the more correct thing to do. Showing KCS joists is the quickest fix but may be overkill? Diagrams are probably more "right" to give, but could be way off when it comes time for construction, especially with actual size and location of RTU not known.