As the subject says, I'm curious if anyone can provide guidance on whether top chord bridging is required once the roof deck is installed.
I found an SJI webinar that discussed bridging at length, and seemed to suggest that the top chord bridging is only for erection and construction loads. It stops short of saying that the bracing can be removed once the deck is in place.
The Vulcraft manual provide similar information. They discuss how bridging needs to be designed for the lateral bracing loads when standing seam roofing is used, since the roofing can't be used to brace the top chord. That suggests to me that in typical circumstances, the deck is doing the work of lateral bracing. But there is a note in the Vulcraft joist manual, at the start of the bridging section, that says "Top and bottom chord bridging is required and shall consist of one or both of the following types..." Unfortunately, deck isn't discussed as one of those options.
I've got a situation where we are trying to reinforce existing joists to resist drifting snow. The method of reinforcing requires plates at the panel points that will interrupt the top chord bracing. I'd like to find a solid reference that says the top chord bracing is not needed. Otherwise, there will be a lot of additional work reestablishing this bracing.
I've searched the forums here, and seen discussion of the deck providing continuous lateral support, but haven't seen any references that discuss this in a way that makes clear that the deck is the only necessary top chord bracing. Any help is much appreciated!
I found an SJI webinar that discussed bridging at length, and seemed to suggest that the top chord bridging is only for erection and construction loads. It stops short of saying that the bracing can be removed once the deck is in place.
The Vulcraft manual provide similar information. They discuss how bridging needs to be designed for the lateral bracing loads when standing seam roofing is used, since the roofing can't be used to brace the top chord. That suggests to me that in typical circumstances, the deck is doing the work of lateral bracing. But there is a note in the Vulcraft joist manual, at the start of the bridging section, that says "Top and bottom chord bridging is required and shall consist of one or both of the following types..." Unfortunately, deck isn't discussed as one of those options.
I've got a situation where we are trying to reinforce existing joists to resist drifting snow. The method of reinforcing requires plates at the panel points that will interrupt the top chord bracing. I'd like to find a solid reference that says the top chord bracing is not needed. Otherwise, there will be a lot of additional work reestablishing this bracing.
I've searched the forums here, and seen discussion of the deck providing continuous lateral support, but haven't seen any references that discuss this in a way that makes clear that the deck is the only necessary top chord bracing. Any help is much appreciated!