spats

Structural
Aug 2, 2002
655
I thought this had come up before, but I can't find anything searching the posts. Why is there a discrepency between the joist weights listed in the "Economical Joist Guide" tab versus the approximate weights listed in the Standard Load Tables in the catalogs? I'm looking at Vulcraft's catalog, but I believe this is pretty universal.
 
Replies continue below

Recommended for you

I generally calculate the moment, and determine the As for the chord by using 0.9 of the joist depth, and calclate the weight and multiply by 3 to accommodate the other chord, and the web. The joist depth (in) is based on 0.7 x the span (ft)... usually gives a pretty close 'guess'.

Dik
 
The Economical Joist Guide weights are Vulcraft's actual joist weights. The Standard Load Table weights are SJI standard weights, which I assume is an average of various joist manufacturers weights for a particular joist.
 
Thanks tadeng... that makes sense to me!
 