I have a light hazard building with Dry wall, 12" bar joists, with 6" of batt insulation on the dry wall and then a wood floor for above. So 6" of dead space above the insulation to the underside of the floor. Would this be considered Combustible Concealed space?
Thanks
 
Replies continue below

Recommended for you

Without seeing it or a cross section

I would say yes combustible concealed space, sprinklers required

Because space is not less than six inches

Add another inch of insulation or something.

See what others say
 
combustible concealed. Add more insulation to avoid sprinklers.
 
So if they add another 1" of insulation I can get away from the coverage
 
It needs to be insulation filled. You can get away with, I believe, a 2" air gap AFTER settling, but that is all.
 
Travis there is the fill option

But if the gap is less than six inches, say five,,, doesn’t that negate sprinklers ?
 
Travis there is the fill option

But if the gap is less than six inches, say five,,, doesn’t that negate sprinklers ?
I believe it is <6" between structural members. I am sure the wording could be cleaned up to truly verify it.
 