Steel Pipe supprtr analysis 2

Status
Not open for further replies.

sidnum

Structural
Jul 14, 2008
13
Hi, i am trying to design a support system for a DI pipe. The system is basically a "U" shape strap over the pipe and the strap is fixed to a support base. I have been able to obtain the forces due to water moving in the pipe (along the pipe & perpendicular to it) and assumed that they act through the pipe center line. However I and some colleagues are having difficulty in understanding how to transfer (or how it tranfers) the perpendicular force (230kN) to our support base and what stresses it causes in the strap by forcing the pipe to move/roll. Please see diagram. We have assumed that the longitudinal force (180kN) will cause a shear and tension on the support bolts due to their eccentricity
PS I am UK/Ireland region based but saw the idea from a US company's web-site. However I am struggling to find some UK/Ireland based standard information. Therefore any suggestions on these types of products would be greatly appreciated. Thanks :)
 
Replies continue below

Recommended for you

Even if your forces are calculated correctly (I didn't check), the only case where you might see thrust at an elbow is if you have unrestrained pipe joints, like push-on fittings. Check the pipe design specification and details for the use of restrained (flanged, mega-lug, mechanically restrained, etc.) joints.
If the joints are flanged or otherwise restrained, all the forces resolve themselves through the lengtrh of the pipe and there's no thrust at the elbow.
 
That is a strange looking pipe anchor. Analysis is difficult with the gap under the clamps. The behavior of the strap on the pipe depends on the pre-tension in the bolts but that appears to be where the moment must be resisted, there are veriables over which, you have no control.

I would expect something like a cross between:

and
With the bottom of the steel on the concrete.

Michael.
Timing has a lot to do with the outcome of a rain dance.
 
Thanks for the reply guys,
The forces were based on 10 bar pressure and a 45 degrees bend, the resultants were taken from a table from a CIRIA report on thrust blocks for pipes

If I removed the gap (and also there are no other forces than those due to the waterr in the pipe) what other variables would there be? I could make some assumptions.Is the analysis any easier or would i be wasting my time without software?
 
I don't understand how you can generate a force of 230kN in each support if the axial component, i.e. P*A is only 180kN. Can you help me with this?